Forum Boilers & Heating UFH manifold losing pressure — can't find the leak
7

UFH manifold losing pressure — can't find the leak

Underfloor heating manifold on a new build keeps dropping pressure. System was pressure tested at 6 bar before screed and passed. Now it's been running a few weeks and drops about 0.5 bar a day. I've checked all the manifold connections — all tight. Screed looks fine, no wet patches. Could it be micro-leaks in the pipe joints under the screed? How would you find it?

2 Answers

8
0.5 bar a day is significant. If the screed looks dry that rules out a catastrophic leak. Most likely you have a slow weep at one of the compression or push-fit connections on the manifold itself rather than in the floor. Get a pressure test kit on it, isolate each loop one at a time and see if the drop stops — that'll tell you if it's the manifold or the floor pipework.
6
Also worth checking the expansion vessel. A waterlogged or failed expansion vessel can cause a pressure drop that looks like a leak. Easy to check — turn off the system, release pressure to zero, and check the vessel pre-charge with a tyre gauge. Should be about 0.5 bar below system fill pressure. If it's zero or water comes out the Schrader valve, you've found your problem.